Hello
I would like to some feed back on an issue we have been dealing with.
Prior to installing a new HART device in the field we have recently begun setting it up on the "test bench" Delta V controller (Ver. 13) and then removing it and installing in the field permanently.
I reached out to EE365 community and was instructed to disable the HART channel, and downloading the card first, then change the A/I device tag back to its original default tag (XX_XXX_CO1CH01) download again then I was clear to remove the device from the test rack.
I tried this procedure when we had to replace a HART flow transmitter that failed recently but unfortunately AMS is not able to scan the newly installed device.
The new device with the newly updated rev. appears in explorer properly, and in AMS as well.
I was able to rebuild the physical hierarchy throughout the AMS network and it also appears at the I/O level in AMS.
Everything looks good for this device except I can’t scan the device, AMS is unable to communicate with the live device......
Is there a procedure that can walk me through step by step on how to put a HART device on to a test rack and then remove it for a permanent installation.
my other question is does anyone else put new HART devices on a test rack to set them up and verify calibration prior to installation.
Thanks