I have just added 2 new workstations to an existing DeltaV network. They will be used primarily for the part of the process in one area. Since I wanted to maintain flexibility on how the workstations are used, I limited access by user privileges. One operator account can access the old part of the plant while a new operator account can access the new part of the plant. While the workstations are getting the proper alarms for their areas, I would like the old and new parts of the plant to have different alarm sounds since they are in the same control room. I see that DeltaV has 2 alarm sound groups for this very purpose. How can I specify that the alarms from one area use the second set of sounds while everything else uses the first set
Alarm Sounds can't be done by areas per say, alarm sounds 'can' be by workstation (with some manual intervention). You can only pick one sound currently in the database for alarm priority sound (nothing about area or workstation), so you have to pick the sound you want and then go to the machines and rename the sound files so that the sound you want to hear the station is named the same as the configuration of the alarm priority.
For example: You configured WSA-High 2010HCS.wav for Critical Alarm
Note: this process is using same names of the files that already exist but you could create a new name wave and select this for alarm priority but you will have to ensure this named file is on all machines manually as the sound folder isn't handled by Yellowpages.
So back to initial request - the only way to get exactly what I think you want is to follow process above for workstations supporting 'new' areas, only have 'old' area(s) assigned to 'old' workstation(s) alarms and events, 'new' area(s) only to the 'new' workstation(s) alarms and events.
Hopefully this was clear enough :D