Hi ,
I am facing issue to connect GE System OPC Client to Delta-V OPC Server.
My Workaround.
Installed OPC Remote in OPC Client, DeltavAdmin account got created, Logged in that user and checked Value in OPCWatchit, Connection was successful and Value started updating in OPCWatchit.
Further Created new OPC User in DeltaV Database, Downloaded setup data to OPC Server and Created Local Windows OPC User in OPC Server.
Did the DCOM Settings Added OPC User in Launching and Access permission of FRSOPCDV in Dcomcnfg.
Restarted OPC Server.
Now Tried to Browse OPC Server from Matrikon in OPC Client Machine, I could able to connect to OPC.Deltav.1 further when I try to Browse Tags , it used to throw error, Error Code is 0x80070005 ,
Checked this error code in KBA, found below answer, But I Double checked the Login Passwords in OPC Client, OPC Server and Delta-V, Everything looks Ok.
General access denied error): If OPCPing works, make sure the user logged in to the client machine has a valid DeltaV account. If the client is run as a service configured with a specific user, make sure that user also has a valid DeltaV account.
In reply to Neil Castro:
In reply to Sathishbabu.bv: