Does anyone know where to find the actual bitstrings assigned to the values of the 'Mode' type parameter as I'm struggling to find these in BOL.
There is a line of code in the PCSD modelock composite:
REQ_MODE_TARGET := REQ_MODE_TARGET > AUTO ? REQ_MODE_TARGET | 16 : REQ_MODE_TARGET;
Where REQ_MODE_TARGET is a 'Mode' type parameter. I know the Mode type parameter is a series of bitstrings with each bitstring representing a mode but in order to fully understand what the bitwise OR operator in this expression is actually doing I need to know what the actual bitstring for each respective mode is.
Many thanks
Adrian Taylor
If you search in Books Online or "mode constant", the first article that comes up is Constants. In that article is a table explaining the DeltaV Mode Contants.
Here is a quick table of the mode constants:
In reply to Sami Uddin :
In reply to AdrianTaylorUK:
In reply to Matt Stoner:
In reply to Martin Rooke: