Unable to display the status of the digital input (1 as "alarm", 0 = "normal") in the graphics

In the graphics configure mode, I copied a working dynamo and pasted it to another page for the alarm status of another device connected to DeltaV DCS.

Then, I changed the parameter and linked it to the module.

The module has no error or whatsoever since the value is good in online mode.

But the new dynamo is in magenta and the value is showing ******.

What could be the problem?

The difference between the two dynamo (the original and the copied one) is just the module reference.

Thanks for your answers.

  • In reply to SBPosey:

    I've been doing this "copy and pasting" of dynamo before and I was 100% sure that there should be no issues.
    Today, as I energized the Proplus and open the graphics, I just found out that the dynamo is working.
    Could it be a flaw in the DeltaV?