We have configured a new workstation, running 13.3, to display on 4 monitors all capable of 1920 x 1080 resolution. I have tried each of the supplied layout files for 1920 x 1080, and each spawns an error message upon startup of Operate in "Run" mode, usually along the lines of "Error no. 9 Subscript out of range". Loading locks up before any pictures are loaded. If launched from "configure", Operate will spawn the errors and then close completely. If launched directly in the Run mode from "start", the application will lock with two gray screens and has to be stopped from Task Manager.
Usersettings.grf has most of the customizations commented out (specifically preload files that might spawn some VB errors).
We have since tried the "DeltaVSquare_OK_Picture_1680x1050.Layout, which functions, and fills all the 1920x1080 screens (auto-scales both 4:3 and 16:10 graphics developed in 11.3.1 and prior versions). Faceplates are huge but all functionality is there. We get the "Alarm List" on screen 2 and "Area Alarm Filtering" on screen 4.
If you have any thoughts about why I can't get Operate to load in a Quad 1920 x 1080 Layout I would be interested . . . .
Thanks,
John
In reply to Verx:
Are you saying there are some other graphics settings, aside from these, that I should be changing? Everything is set to 1920 x 1080.
In reply to John Rezabek:
Update: With corrected screen order, the behavior is unchanged (hangs at "14"on progress bar, Error 0).
This resolution setting is the same - both before & after. I will give your suggestion a try. I commented out every line in "CFixPicture_Initialize" in WSNAME_Settings.grf and now I get a different error:
Note the distortion . . . it hangs here but allows me to Ctrl+W back to configure mode.
Update: Renamed the default Usersettings file for this WS and now 1920 x 1050 quad layout will launch without errors. However faceplates are either huge and spread out (primarily our custom faceplates that have been migrated and augmented through successive releases since version 4 / Fix32) or the faceplates are "squeezed" (for example, the FRS faceplates for MPC controlled & manipulated variables). Many of our other "popups" are distorted (spread out) and any "main picture" created in 4:3 format and opened in Operate "Configure" mode is badly distorted (spread out). "Detail" displays are large (they take up half the screen) but the distortion, if any, is not very noticeable.
In reply to Joe_blow444:
In reply to Dave Denison:
Dave - it is unchecked. I did use the User_ref file to reconstitute a "clean" settings file, which succeeded in getting 1920 x 1080 to function (launch without errors or lockups). Joe - We have been using 1680 x 1050 since switching to wide screens a few years ago - agree there is minor distortion but nothing like I am seeing with the 1920 x 1080 layout. Actually, the old 4:3 "main" graphics are no more stretched or distorted in "RUN" mode that they appeared in the 1680 x 1050 resolution. But "configure" mode is totally useless for the legacy screens. Configure works fine in 1680 x 1050 (windows graphics drivers and DeltaV layout) - I can create and edit both 4:3 and 16:10 aspect ratio graphics. Not so with 1920 x 1080. I am trying to make the most of a 65" overview screen and I was hoping to utilize the higher resolution. If this continues to fail we may have to revert to 1680 x 1050.
Update: Unchecked both "Bypass 16:9 layout" and "Wide Screen Display" and the distortion seems to go away . . Trying different 1920x1080 "Layout" files - "Run" always loads the same pictures regardless of the "Layout" file - why? Here are a few examples of what's being loaded versus what's in the "Layout" file e.g. "DefualtSquare_1920x1080.Layout (renamed to "WSNAME_Picture.Layout):
I tried checking and unchecking the "Large Screen Display" in "DeltaV User Settings - this changes what initial pictures load but still seems to ignore the "Layout" file.
When "Large Screen Display" is checked, that's when the "TenFootUI*" standard banners and toolbars load . . .
Also tried checking and unchecking the "bypass 16:9 Panel Layout", with similar systems . . . something a little different loads each time but still nothing like what's specified in the "Layout" file.
[Default Pictures]
Count =29