HART Device Specific Detail Displays

Where can someone find device specific detail displays for HART devices (the ones used instead of HARTgeneric_dt.grf )?  Specifically I'm looking for the 3051S Wireless HART pressure transmitter, but really I'd like to know where to find any of these.

  • Have you got AMS Intelligent Device Manager? It is an intelligent device management (IDM) software that displays all FOUNDATION fieldbus, 4-20 mA/HART, and WirelessHART devices with their full details. Learn more about IDM here:
    www.eddl.org/.../
  • You are looking for the DeltaV Operate detail displays that were originally released in v8 for DeltaV SIS. These displays were specific to each device type. The standard HART status BYTE is common to all devices, but the additional diagnostic values are custom to each device. I think these were created because AMS Inside only supported FF devices at the time, so these were created to provide access to the SIS Device health information without the requirement to purchase a full featured AMS Device Manager system. The displays mimicked the DD screens but only provide read access. There was also a limited number of approved safety devices available.

    In later releases, AMS and DeltaV were reunited and full diagnostic coverage of FF and HART devices were provided with the same AMS. The use of these displays was pretty much discontinued. Todays EDD screens are completely different and going back to the DT.GRF file would not be a viable approach. Also, within the standard Device Faceplate, there is a button (A Fisher valve and Rosemount transmitter) that will launch AMS Device Manager and connect to the device directly to show the Device health. As Jonas suggests, you should look to AMS Device Manager to view and manage HART devices.

    You would need to create your own device Detail Displays if you want to use this approach, and I don't recommend that.

    Andre Dicaire