Running DeltaV 11.3.1, WS04 hotfix
We have 5 stations and a ProPlus in a workgroup. Recently we made a changed which faceplate is being used on a module that I'll call 2FI2000 from "A_AI" to "A_PID". When we try to open the faceplate for 2FI2000 on station 2 it opens "A_AI" while Stations 1, 3, 4, 5, and the ProPlus all open "A_PID", like they should. Station 2 was working properly yesterday when we were performing the same tasks.
We have rebooted this station, and downloaded every part that can take a download, and have done the same to the ProPlus. We have also downloaded the setup data for the controller that it is on.
I would prefer to not need to run workstation config on it again.
Does anyone know what controls which faceplate is opened for each module? Since it doesn't seem to read it from the database for each request.