Hello,
My Event Chronicle stop recording data in November 26.
When I configure parameters to show history data from earliest to latest, the latest data stop on November 26 2014.
Can someone please help me to retreive previous data to-date and how to prevent this from happening again?
Thank you kindly.
It is likely that you do not have your chronicle set up to automatically create current data sets.
In the Advanced tab of the Event Chronicle Configuration, you probably have the Current Event History Data Set Total Storage Target set for 0.
Now according to documentation, the active should still record data in this scenario, overwriting the oldest data first on the active chronicle, so perhaps you have a different problem.
Are you sure you are looking at the active data set in PHV? That is the default, but it is possible that you are not. In PHV look at Events-->Configure Events and make sure the Active on the proper chronicle is selected.
In diagnostics, what is the state of the Alarms and Events subsystem (ECHRON) on the chronicle server?
Open Event Chronicle Administration and see if you have any current data sets, and what the storage capacity and state of the active chronicle is.
Moving forward, I would suggest enabling at least one more chronicle, so that the data is not lost. I'm not sure you have any recourse restoring the data at this point, however.
Thank you Youssef for responding. Responses to your questions above.
1. The Event Chronicle is setup on the Pro-Plus and Diagnositcs shows the state of ECHRON as GOOD. diagnostics also show the ECStop is NO, which means the Event Chronicle has not stop recording. Excess disk space is show alot.
How do I start the Event Chronicle to collecting data again?
Here is the options in Configure Event Chronicle.
Events Data: Proplus, localhost,
Events: Current is from 5/2/2014 to 5/21/2014. Active from 4/2/2014 to 11/26/2014
I am not sure why my Current does not have more data sets then just one. I am also not sure why stop recording on 11/26/2014
In Diagnositcs, I notce the HDSXSMB (Excess disk space) is 1.52165E+006, and my Active Event History Data Set Storage Target is 4000Mbytes. As Youssef mentioned the system should automatically delete old current data sets once the storage size is full and continue colleting data for the new active data set.
But for some reason data collection stopped in November.
In reply to Ray Emerson:
In reply to DCS Newbie:
Thiago Borba
In reply to Thiago Sousa Borba: