Futrnic signal anlg

I have Emerson EIM TEC2000, now I have a problem that's analog input and output not same , in auto operation if input set to 0 percent but output going to 27 percent, how can I calibrate this problem ( I am using analog mode)...................thank you

  • Herwan, In order to answer your question I will need the S/N of the unit so that I can look up the WD and see the setup you have.

    Nelson Zepeda | Service Manager | Valve Automation
    Emerson Process Management | 13840 Pike Road | Missouri City | TX | 77489 | USA
    T + 1  281-403-4136 | M + 1 281-546-3827

  • In reply to Nelson:

    Thanks Mr.Nelson, this is S/N 129246A01, Model SLQK-503R, Please give me an answer step by step how to calibrate analog to be same input and output
  • Hello Herwan, to clarify your question, do you send your command remotely (ex. DCS)? I have sent you a separate email on the procedure on how to calibrate the actuators analog input/output functions.
  • Hello Herwan. We have 2 types of actuator 1. On/Off and 2. Modulating. We have checked your actuator based on the S/N.

    The actuator that you have installed is an On/Off type whereas the function that you require is Modulating type.

    In order for you to achieve that function, you will require a ACM - Futronic module.

    We have a local business partner that can assist you with this or you can reach me at below details.

    Dexter Huerto Jr.
    T +65 65014634 | M +65 90129259
    [email protected]
  • In reply to Dexter Huerto Jr.:

    Thanks Mr.Dexter, I have fixed the problem now analog input and output is same, but I have new problem when setting SV cannot setting low than 3 digit (actuator not moving) only can moving if SV Set more than thee digit, what's parameter I have to re setting ?
  • Hello Herwan. Can you take some screen shots or actuator photos for us to have a better understanding of where you are seeing this problem?