Multi spot temp sensor and water level sensor connection

Previously 29XX and 39XX used in plant.  We upgraded to Raptor but not sensor only electronic module. Water level sensor was 4 to 20 mA HART analog input. But MTT does not have this 4-20mA . Now I want to connect water level sensor to MTT.

(MTT having option RS 485 connection for water level sensor)

Any possibilities are there to connect MTT(Multi Temperature Transmitter).

1 Reply

  • Dear Rajesh,
     
    The easiest way is to change the existing MSTW to a new 765 sensor.
    There is no mechanical difference between the old and the new sensor and the existing flange fitting can be reused.
     
    Best Regards,  Johan Sandberg
     
     
     