ADB error n a 3144 with Foundation Fieldbus,

In a 3144P with Foundation Fieldbus what does "ADB Transducer Block Error" means? This error appears in a transmitter with also de SPM error.

The transmitter is a demo unit we use for trainings,

1 Reply

  • Hi,
    have you checked that no one have changed the settings in the transmitter?
    http://www2.emersonprocess.com/siteadmincenter/pm%20rosemount%20documents/00809-0100-4021.pdf see 153 and check that the values are correct and you are using the same scaling on the other side.
    hope this helps?