EmersonProducts

Hi Everyone ,

I have got few questions

1- Is loop powered dc available in 8732 transmitter

2- Do Emerson supply 64 inch mag meters as i see that saline water companies tend to have these large size requirements

3- Also do Emerson supply clamp on ultrasonic meters , having seen cement companies using clamp on ultrasonic for 12 inch line size,is there any approach we can persuade the customer to use emerson meters for this

Thank you

Yunus 

3 Replies

  • Yunus,

    I can provide some insight on your questions relative to the magnetic flowmeter products.

    Answer to question 1 – No, we do not have a 2-wire mag product at this time. For customers concerned about power consumption, we do have a low power option. Details can be found in the product data sheet available on Emerson’s website.

    Answer to question 2 – While we do not manufacture sensors larger than 48-in, we do have the ability to supply larger sensors through various relationships that we have with other manufacturers. This allows us to supply the full breadth of requested mag sizes on projects.

    Feel free to contact me with any additional questions regarding Emerson's magnetic flowmeter product offering.

    Trever Ball
    Director of Product Management
    Emerson Magnetic Flowmeters
  • In reply to Trever Ball:

    Yunus,

    I also received some information from our Ultrasonic team regarding your 3rd question.

    Emerson has a partnership with FLEXIM on offering clamp-on ultrasonic flow meters to complement our portfolio of flow metering technologies, services, and solutions. Our regional flow consultants/sales teams can help you select the right flow. If you are interested, your Flexim distributor can be found in the link below.

    www.flexim.com/.../middle-east-africa

    Thanks,
    Trever
  • In reply to Trever Ball:

    Thank you Trever for the reply .