Emerson Exchange 365
Search
User
Site
Search
User
State
Verified Answer
Replies
2 replies
Subscribers
5469 subscribers
Views
6999 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Derek Thomas
30 Oct 2020 7:44 PM
Industrial Edge Computing — Enabling New Capabilities
0 Replies
Deanna K Johnson
27 Oct 2020 10:27 PM
We Speak Your Language: New Translated Pages on Emerson.com
0 Replies
Deanna K Johnson
22 Oct 2020 7:07 PM
New PACMotion Revolutionizes Motion Control Flexibility, Scalability and Reliability
0 Replies
Alejandra Camacho
16 Oct 2020 6:22 PM
On-Demand Webinar: Edge Controllers Enable Digital Transformation in the Oil & Gas Industry
1 Reply
Cambie Ling
14 Oct 2020 2:43 PM
RXi Panel PC Wins Accolades for Innovation
0 Replies
<
>
Similar Posts
Disabling USB Port
Disabling HDD, USB ports on Delta V worksation
Servers do not have PS/2 ports or parallel ports. Will require the use of a USB DeltaV dongle Environmental
Live, database backup
System Backup Utility
Share
Answered
IC695CRU320 backup to USB?
Is this redundant CPU capable of USB backup of program and config?
All Responses
Answers Only
Steve Ward
11 Feb 2021 5:03 PM
IC695CRU320 is an older CPU that does not support USB program backup/restore. You could consider upgrading to the IC695CPE330, the IC695CPE330 does support USB program backup/restore.
Robert Wimmer
11 Feb 2021 6:07 PM
In reply to
Steve Ward
:
This is what I thought, thanks!