IC695CRU320 backup to USB?
Is this redundant CPU capable of USB backup of program and config?
All Responses
Answers Only
Steve Ward
11 Feb 2021 5:03 PM
IC695CRU320 is an older CPU that does not support USB program backup/restore. You could consider upgrading to the IC695CPE330, the IC695CPE330 does support USB program backup/restore.
Robert Wimmer
11 Feb 2021 6:07 PM
In reply to
Steve Ward
:
This is what I thought, thanks!