Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5477 subscribers
Views
7981 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
rick li
19 Oct 2021 1:06 AM
OPC
0 Replies
Sebastian
1 Oct 2021 5:58 AM
DeltaV Excel Add-In issue
4 Replies
Stuart Jolley
29 Sep 2021 4:46 PM
Profibus Signal
5 Replies
Jarod Howard
23 Sep 2021 5:58 PM
Deltav Operate Crashes with no errors or alarms
2 Replies
Donal Costello
23 Sep 2021 1:58 PM
VIM2 Communication Issues
0 Replies
<
>
Similar Posts
<div dir="auto">Explorer open in OS station without dongal</d
Action block's expression writes to PCSD based FF-AO block to change Auto to CAS and its results no change of mode means its stays in AUTO mode.
Auto Logoff DeltaV
Auto Removal of Batch
Auto Logoff DeltaV Operate
Share
<div dir="auto">Hello professionals,<div dir="auto"><br /></div>
Hello professionals,
Greetings of the day!!
I am working on projects where RIU(Remote interfacing Unit) are use.
While testing the communication I am facing a situation which I am unable to understand.
If my both network cable is removed from the RIU scanner then I am getting a not communicating Alan's on the alarm list and events.
But if I open PHV(process history View) of one of the AI module which is communicating from the same the RIO Iam getting a modbad alarm and my AI is holding up the last value.
As a result once the communication is restored back to normal then there bis no discontinuity in trend.
Shouldn't we have got do data there.!??
I really appreciate a response which will help us improving our understanding and concept.
1 Reply
Andre Dicaire
29 Jan 2021 4:41 PM
The AI Block has set the BAD status indicating the value unsuitable for automatic control, but it also holds the last known value. Normal Function block behavior on a downstream PID would be to shed its mode to manual to prevent unwanted windup of the loop, all built in features.
Status of values is an important feature of DeltaV, allowing your control modules to respond accordingly. Note that with DeltaV Continuous Historian, the Status of the signal is also captured and you can set the PHV trends to indicate when the value is BAD. The Status field is described in Books on line in greater detail.
Andre Dicaire