HI ALL
Could we do Bulk edit automatically or not.
2 Replies
rhamlin
17 Jun 2020 12:18 PM
Not sure what you mean by automatically. You have to create a user defined format, export a module to create a .txt file with your format file, then you can edit and reimport. The only "automatic" action is that DeltaV is taking the .txt file that you defined and bringing it into deltaV explorer.
PRASHANT-MUTTEPAWAR
17 Jun 2020 2:37 PM
Hi
Bulkedit means ,creating control modules and update the things which are used in the control modules by using below method . So we can do bulkedit automatically.
Regards
Prashant