In DeltaV Operate every module are working fine except Discrete Valve Module.When i open faceplate of this type module then DeltaV create error : RT_NULL_ITEM and faceplate permit option has gone to ESD mode.Please find below screenshots of error and warning ::
As a result i can not use these type of module from DV graphics page.Does anyone have any idea why this is happening?
2 Replies
Lun.Raznik
11 May 2020 4:05 PM
Can you try to read the parameter using OPCWatchit? Replace A_CV with just CV.
Jason.Brumfield
16 May 2020 3:38 PM
Is this a custom faceplate or out of the box and did you rename the DC block in the module to something besides DC1?