Emerson Exchange 365
Search
User
Site
Search
User
Replies
2 replies
Subscribers
5477 subscribers
Views
10602 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Eric Franco
29 Apr 2026 3:51 PM
SIS write connection issue
1 Reply
KeithHarms
22 Apr 2026 7:07 PM
Virtualized DeltaV system Backup options.
3 Replies
Shaswat Raj
21 Apr 2026 6:30 AM
PK100 Not able to communicate over Ethernet/IP on different assembly instance other than 101,100,102
8 Replies
Jesse Klupfel
12 Apr 2026 10:01 PM
Tesys Island Profibus Configuration in DeltaV
1 Reply
Eric Franco
7 Apr 2026 1:51 AM
PCSD Class Simulation Alarm "FALSE SIMULATION" Alarm
0 Replies
<
>
Share
Faceplate_Error
In DeltaV Operate every module are working fine except Discrete Valve Module.When i open faceplate of this type module then DeltaV create error : RT_NULL_ITEM and faceplate permit option has gone to ESD mode.Please find below screenshots of error and warning ::
As a result i can not use these type of module from DV graphics page.Does anyone have any idea why this is happening?
2 Replies
Lun.Raznik
11 May 2020 4:05 PM
Can you try to read the parameter using OPCWatchit? Replace A_CV with just CV.
Jason.Brumfield
16 May 2020 3:38 PM
Is this a custom faceplate or out of the box and did you rename the DC block in the module to something besides DC1?