Emerson Exchange 365
Search
User
Site
Search
User
Replies
2 replies
Subscribers
5477 subscribers
Views
10620 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
hagouda
26 Aug 2025 5:38 PM
Random lose of series MQ controller Redundancy
4 Replies
Dan Mos
19 Aug 2025 9:45 PM
Allen Bradley E-300 Device net configuration issues
3 Replies
hagouda
19 Aug 2025 3:32 PM
timeout between processor 2 and i/o processor 2 in SLS1508
0 Replies
ha nguyen
15 Aug 2025 8:17 PM
Conventional Software Support - End of Life - Guardian Support Bridge Service
1 Reply
Kent
15 Aug 2025 7:29 PM
Fast Temperature Measurement
1 Reply
<
>
Share
Faceplate_Error
In DeltaV Operate every module are working fine except Discrete Valve Module.When i open faceplate of this type module then DeltaV create error : RT_NULL_ITEM and faceplate permit option has gone to ESD mode.Please find below screenshots of error and warning ::
As a result i can not use these type of module from DV graphics page.Does anyone have any idea why this is happening?
2 Replies
Lun.Raznik
11 May 2020 4:05 PM
Can you try to read the parameter using OPCWatchit? Replace A_CV with just CV.
Jason.Brumfield
16 May 2020 3:38 PM
Is this a custom faceplate or out of the box and did you rename the DC block in the module to something besides DC1?