Emerson Exchange 365
Search
User
Site
Search
User
Replies
2 replies
Subscribers
5477 subscribers
Views
10620 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Dave Harmon
1 Dec 2025 6:37 PM
DeltaV AO block output wont change
3 Replies
Rawlz
7 Nov 2025 12:51 PM
Replacing Foundation Fieldbus Tank Radar Device
0 Replies
Donald Dron
4 Nov 2025 9:04 PM
Next Gen Smart Switches
4 Replies
Tomas Grepl
18 Sep 2025 9:51 PM
PCSD PWM Control vavle and PCSD graphics
4 Replies
Patrick J Rossi
16 Sep 2025 2:04 PM
Controller performance metrics: parameters to trend and examine, what are most critical?
1 Reply
<
>
Share
Faceplate_Error
In DeltaV Operate every module are working fine except Discrete Valve Module.When i open faceplate of this type module then DeltaV create error : RT_NULL_ITEM and faceplate permit option has gone to ESD mode.Please find below screenshots of error and warning ::
As a result i can not use these type of module from DV graphics page.Does anyone have any idea why this is happening?
2 Replies
Lun.Raznik
11 May 2020 4:05 PM
Can you try to read the parameter using OPCWatchit? Replace A_CV with just CV.
Jason.Brumfield
16 May 2020 3:38 PM
Is this a custom faceplate or out of the box and did you rename the DC block in the module to something besides DC1?