Emerson Exchange 365
Search
User
Site
Search
User
Replies
6 replies
Subscribers
5476 subscribers
Views
31511 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
zanjurne.deepika
22 Sep 2022 8:29 AM
Charm integrity error flooding alarms and events
7 Replies
s_brwn
20 Sep 2022 2:35 PM
User Level required for Operate and Windows Shutdown
1 Reply
kathrynpate
19 Sep 2022 7:20 PM
Emerson Exchange
0 Replies
barka
15 Sep 2022 10:22 AM
Read DeltaV Control Module Scan Rate
4 Replies
TreyB
1 Sep 2022 8:06 PM
External reference with class module error
4 Replies
<
>
Similar Posts
Extract the logs on an SLS with telnet
Fwd: Net work binding when using 4 NIC
Emerson Exchange 2019 DeltaV Controller and I/O Hardware - Product Update sessions
Be sure to get to the DeltaV roadmap sessions
Control Studio Phantom session issue
Share
Fwd: Telnet session with DeltaV Controller
From:
krishna sen
<
[email protected]
>
Date: Sun, May 10, 2020 at 12:19 PM
Subject: Telnet session with DeltaV Controller
To: <
[email protected]
>
Dear all
Please let me know how can i open a telnet link with MQ controller and look in the Hardware event log ?
6 Replies
Hassan.hameed
10 May 2020 9:06 AM
You can go through diagnostic and select the required controller and right click select telnet after that follow list appear
krishna sen
10 May 2020 9:40 AM
Many many thanks for reply. Can I open telnet link with controller through command prompt ? If yes then what is the linking procedure.
Hassan.hameed
10 May 2020 9:53 AM
In reply to
krishna sen
:
No you cannot only from deltav explorer diagnostic can access to the telnet
krishna sen
10 May 2020 10:21 AM
Thx
Lun.Raznik
11 May 2020 3:41 PM
In reply to
krishna sen
:
telnet IP should work. For example, if IP of the controller is 10.4.0.10, then telnet 10.4.0.10 will open session to the controller.
Jason.Brumfield
16 May 2020 3:44 PM
as an adder, if you have redundant controllers, you have to drill down to the standby in diagnostics to remote the non active controller, each one has it's own telnet logs.