Emerson Exchange 365
Search
User
Site
Search
User
Replies
6 replies
Subscribers
5476 subscribers
Views
31521 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Invalid String
1 Sep 2023 8:40 AM
DeltaV Simulate V15 Virtual Machine Help
3 Replies
Y H
28 Aug 2023 6:41 PM
DeltaV comms to Wonderware Historian
1 Reply
Invalid String
26 Aug 2023 8:21 PM
M Series Serial Card - Series 2 | Bad status | Reads work and writes don't?
2 Replies
Yogeshwar Patil
21 Aug 2023 1:18 PM
Facing Issue with Hotfix installation DeltaV_1431_WS_28_CSS
2 Replies
Jenny La Bounty
15 Aug 2023 5:40 PM
Bult Export Interlock Cause & Effect
2 Replies
<
>
Similar Posts
Extract the logs on an SLS with telnet
Fwd: Net work binding when using 4 NIC
Emerson Exchange 2019 DeltaV Controller and I/O Hardware - Product Update sessions
Be sure to get to the DeltaV roadmap sessions
Control Studio Phantom session issue
Share
Fwd: Telnet session with DeltaV Controller
From:
krishna sen
<
[email protected]
>
Date: Sun, May 10, 2020 at 12:19 PM
Subject: Telnet session with DeltaV Controller
To: <
[email protected]
>
Dear all
Please let me know how can i open a telnet link with MQ controller and look in the Hardware event log ?
6 Replies
Hassan.hameed
10 May 2020 9:06 AM
You can go through diagnostic and select the required controller and right click select telnet after that follow list appear
krishna sen
10 May 2020 9:40 AM
Many many thanks for reply. Can I open telnet link with controller through command prompt ? If yes then what is the linking procedure.
Hassan.hameed
10 May 2020 9:53 AM
In reply to
krishna sen
:
No you cannot only from deltav explorer diagnostic can access to the telnet
krishna sen
10 May 2020 10:21 AM
Thx
Lun.Raznik
11 May 2020 3:41 PM
In reply to
krishna sen
:
telnet IP should work. For example, if IP of the controller is 10.4.0.10, then telnet 10.4.0.10 will open session to the controller.
Jason.Brumfield
16 May 2020 3:44 PM
as an adder, if you have redundant controllers, you have to drill down to the standby in diagnostics to remote the non active controller, each one has it's own telnet logs.