Emerson Exchange 365
Search
User
Site
Search
User
State
Not Answered
Replies
1 reply
Subscribers
5474 subscribers
Views
13339 views
Users
0 members are here
frs
script
VBA
DeltaV
Recent DeltaV Community Connect Discussions
Andre Dicaire
9 Dec 2025 3:04 PM
How do you manage History data when you have two or more Historians on your system collecting different Plant Areas?'
3 Replies
Andre Dicaire
3 Dec 2025 11:09 PM
User input required on the DeltaV Enhancement page and vote on the ideas you want to see
7 Replies
Jenny La Bounty
3 Dec 2025 3:53 PM
Phase Logic Module Restart Location
7 Replies
Dave Harmon
1 Dec 2025 6:37 PM
DeltaV AO block output wont change
3 Replies
Rawlz
7 Nov 2025 12:51 PM
Replacing Foundation Fieldbus Tank Radar Device
0 Replies
<
>
Similar Posts
What is the exact difference between the Unit Parameters and Recipe parameters?
Differences between MX and MQ Controller
Difference between Discrete and Boolean parameter type
Plant Messenger- Difference between Events and Alarmsp
Basic difference between Abort & Stop Command
Share
Not Answered
Whats the difference between frszExpertReplacePic and frsReplacePictureOnScreen ?
Whats the difference between frszExpertReplacePic and frsReplacePictureOnScreen ?
frs
script
VBA
DeltaV
1 Reply
Andre Dicaire
19 Nov 2019 4:25 PM
The frsz expert is a configuration tool represented by an icon in Configure mode, and it facilitates creation of a script to replace a picture. It presents a dialog from which you can pick the action you want and creates the supporting VBA code and associates it with a click action on the selected object, such as a text field or an arrow.
The frsReplacePictureOnScreen is a function that you can use in a custom VBA script to replace a picture at run time. You might have logic such that when something specific happens, you want a particular picture to be opened in one of the Display areas. The frsReplacePictureOn Screen could be a function that is used in the VBA script created by the frszExpertReplacePic.
In BOL, search for DeltaV Operate Experts. You'll find an explanation of the dialog. But the main difference is that the frszExpert functions allow you to create custom actions on objects without having to actually code any VBA.
The frs functions are used in your custom VBA scripts so you can roll your own customizations. Note that functions created by the frszexperts are structured and known to Emerson, which allows for these to be migrated automatically, since the function and structure are fixed. Custom script is not migrated and requires manual intervention to understand the intent of the code before one can determine how best to implement it in a new scripting language.
So use the Experts in Configure when you can as this makes your display better supported moving forward.
Andre Dicaire