We had an issue last night with an 8-channel RTD card, where tightening a loose wire on an RTD (ch.8) caused the temperature indications to fluctuate drastically on channels 5, 6, and 7. Very minor interference was seen on channels 1-4. These are all 3-wire Pt.100 RTDs. Our technician for the other side of the plant has seen similar behavior on an RTD card when one of the RTD wires get shorted while connected to the I/O card. His solution was to install transmitters and wire into an analog input card. Has anyone else seen this behavior? Is there another solution to this issue? We are short on space in the existing cabinet and I'm looking for other options.
Thanks,
Kathy
Kathy Pate
Toray Carbon Fibers America
Decatur, AL 35601
[email protected]
In reply to Darrell Cole:
Andre Dicaire
In reply to kathrynpate:
In reply to Curtis Byrd:
Hi Curtis -
These documents were sent to me from Emerson when I had the open call. See page 10 of the .pdf for the discussion about the card having 2 shared "A/D" converters. I see no copyright on these documents so I think they are ok to add here. Hope this helps:)
Fundamentals of Temperature Measurement using RTD and TC.pdfField Wiring recommendations.docx