Not Answered
split 32 dint to 8 -byte
Hello,
i need to split 32 dint to 4 x 8-byte integers. Could someone help me?
Greetings.
1 Reply
Maarten van der Waal
9 Jan 2019 5:50 PM
Look in the question "How to Map 32 bit data in Deltav" for your answer.
For your subject the 32 bits is split into 2 * 16 bits, but using the methods described you can easily split into 4 * 8 Bits