Hi,

When you do some Picture changes it´s important to do the changes on the "master" picturefile from the Proplus, and then upload and download to all workstations.

May I have the same filosofy with the User.fxg file?

If I want to do some changes do I have to take the User.fxg file from the Proplus, and not the local one?

The User.fxg file have diffrent timestamps on diffrent workstations, why?

I have seen that the timestamp updates when you close Operate, after download WS. 

What are your procedure of working with User.fxg file?

Thanks in advance.

2 Replies

  • Yes. You need to use same philosophy.
    Ideally if pro+ and other workstations are synchronized or connected in DeltaV Operate environment then Timestamp should be same.
    Need to check whether all workstation are synchronized and downloaded.
  • In reply to Mantri_Bhushan:

    Whether user.fxg is propagated to other workstations is an option that can be changed by using the Exclude_User_fxg.cmd and Include_User_fxg.cmd in D:\DeltaV\DVData\YellowPages

    This might explain the different timestamps on different workstations