DeltaV Operate WindowName and Main Picture Errors

Hello, I just moved a PIC folder from one machine to another, both version 13.3.1, and whenever I try to open a graphic, the Error: "Error Number: -2(FFFFFFFE) Method 'WindowName' of object 'IFixDocFrame' failed" after clicking ok on that warning the message

"Reset Operator Interface

The picture just loaded into the Main window is not a main window picture. Functions that would normally replace the picture in the Main window will no longer work. Would you like to open the default layout now to reset the Operator Interface environment?

The inital "DeltaV.grf" file will open, but when I created a copy of it and tried to open that one it would not work. I checked the VariableGroup as suggested in other questions but all the files had that group. In addition, I have the correct settings file but the directory does not open.

Thanks for the help, please let me know anything I should try to do to fix this.

OMB

  • Just set a new pic folder from C drive and then Replace PCSD Library as per guidlines of PCSD demo imports which is uploded on PMO site.
    In that they have given sequence of PCSD files to be replaced. With some Unregserver/workspace command which need to run after importing of PCSD.
    After that i hope no error will come. And then this will be the Complete PIC folder without error. So you can just copy your .grf file and project related files.
    I believe it will work.
  • In reply to bhushan619:

    That worked great, thanks!
  • PIC folder should never be copied from one machine to another. Only Project related entities should be copied from one machine to another.
    e.g a new facplate ABC is created/modified then only this facplate should be copied to destination machine.