All datalinks go to &&&&; Event Journal shows flurry of ACN COMM events between various nodes

Beginning at 5:45 this morning, the event journal started recording numerous "ACN COMM" events concerning a variety of nodes. All nodes are wired copper to 24 port R100 switches. Every node experienced between 200 and 700 such events (e.g. "Switched to Secondary ACN" , "Device Connection Failure", etc.) I don't know if it's significant - the only nodes with no such events were 1420 WirelessHart gateways that come in over fiber to port1.1.

Within 30 minutes the board starting seeing their DeltaV Operate graphics DataLinks go to "&&&&&". Then the data would reappear after 5-20 seconds. One station was rebooted after the &&&&& lingered.

No diagnostics of note on the switches - only a couple "Port High Utilization" on the Secondary switch.

Another workstation that had a persistent "BAD" communications on its secondary was rebooted, which cleared that error. Since then the ACN events have stopped (knock on wood).

I have a case open with GSC . . . anyone seen this?

  • Yes, we saw this two weeks ago after installing DeltaV hotfix WS_06. If you have any node that has either Primary or Secondary network not communicating, this behavior will occur. We had a Pro station only connected on Primary, so I disconnected it completely and the communication issues stopped. If you can disconnect the node, that is your quickest solution.

    Our permanent fix was to uninstall WS_06 and install WS_05.

    Kathy

    Kathy Pate

    Toray Carbon Fibers America

    Decatur, AL 35601

    [email protected]

  • In reply to kathrynpate:

    Sorry, I should have been more specific. This was on v13.3.1

    We saw the exact same response as you described. I'm curious if you have WS_06 installed for 13.3.1 or something else? I think its only been out for a month maybe? I would have thought that Emerson would have "recalled" it after our problem considering the issues on operator stations. Good luck! I hope you can resolve your issue as quickly as we did. We were lucky that there weren't any critical operations going on that day.

    Kathy Pate

    Toray Carbon Fibers America

    Decatur, AL 35601

    [email protected]

  • In reply to kathrynpate:

    Kathy - many thanks. Our situation precisely, although we have had WS_06 deployed since 4-Nov and didn't see the issue until this morning. Likewise we isolated it to a node with Secondary ACN problems and have shut it down. If you were able to share your call ID, I would be interested to share it with the GSC. We need the WS_06 hotfix since it prevents random crashes of Workspace.exe . . .
  • In reply to John Rezabek:

    The call number is AC-1701-1652, status is "investigation ongoing". Glad you were able to fix the problem quickly. It was a little scary when we saw it here.

    Kathy Pate

    Toray Carbon Fibers America

    Decatur, AL 35601

    [email protected]