Want to know Default Server Password
Hello,
Kindly share your opinions on below query.
I want to know what Password get set when someone Press button "Set as default" while setting up Server password.
Is there is utility available to detect the same.
Thanks in advance.
Thanks & Regards,
Chetan Bhangale.
1 Reply
Matt Stoner
24 Aug 2017 12:58 PM
The only Utility is the one that can be used to change the password.
It is called ServPwd and is located in the DeltaV/bin directory and you will be required to run it on all machines if you are changing the password.