Emerson Exchange 365
Search
User
Site
Search
User
Replies
3 replies
Subscribers
5480 subscribers
Views
9320 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Steven Kang
22 Sep 2021 11:53 AM
VCAT Functionality
1 Reply
s_brwn
20 Sep 2021 12:12 PM
120 VAC DI Isolated Charms not changing state- Always On
7 Replies
SimHogan
15 Sep 2021 4:55 PM
Help diagnosing: mA error seen at the DeltaV AI CHARM
19 Replies
Shamusk
31 Aug 2021 6:00 PM
Sequence (SFC) Programming Standards
7 Replies
CuriousDuncan
27 Aug 2021 11:59 AM
Error while downloading
1 Reply
<
>
Similar Posts
Low Profile small PLCs
Alarm : Event Chronicle : Disk Space Low
VIDEO: Modernize Your Plant with Low Risk (PLC 1771 CPU Reaches End of Life)
Press Release: Emerson to help North West Redwater reduce emissions at advanced, low-carbon refinery
Selecting Control Response
Share
CTLS Low Select
Question:
How does the CTLS block Limits the output of the non selected PID block ? It seems like the output of the non selected PID block is somehow fixed by the BKCALC of the selector block.
Status:
I have a very simple low select CTLS which selects between a PIC and a FIC.
Output value of the my FIC is %16 and the PC is %47.
Output of my CTLS block is of course %16
%16 is entering the BKCALC of my PC and FC
What I want to know:
Although the Setpoint of my PC is 2000 and the current PV is at 1500, the output of the PC is not ramping up towards %100. It seems like it somehow has been fixed to 47. it moves very slightly but I expected to move a lot faster. Does it have anything to do with the CTLS affecting the PC block? I don't see any tracking logic on the PC. The Action and Gain of my PC is correct.
Regards,
Learner
3 Replies
Matt Stoner
21 Jan 2016 3:14 AM
Learner,
Yes the Control Selector Block is sending a BKCAL status to the non selected loop that it is not selected and this is what is not allowing the PC loop output to increase. It won't allow the not selected loop to keep increasing the output as it will never get selected by going higher. If the PC loop does become the selected loop, the output will increate as you expect.
Regards,
Matt
Former Member
21 Jan 2016 10:18 AM
In reply to
Matt Stoner
:
Learner,
I think the BKCAL status provides an anti-reset windup function so that the pressure controller doesn't just keep on winding itself open, as the actual selected output from the CTLS module is limited to the output by the FIC. If both the FIC and PIC were to increase output, the CTLS module would take which ever one was increasing the slowest (as it would be the lowest value at somepoint) and keep the system in control.
Regards
Col
Andre Dicaire
21 Jan 2016 1:30 PM
In reply to
Former Member
:
The back cake status tells the PID to disable reset and uses the bkcal_in value for the integral term. The OUT value of this PID therefore responding only to the error with proportional action. It is more than anti reset windup.
The out value will respond to change and as the error approaches 0, the OUT value will approach the CTS output for a bump less cross over if the PID error goes the other way.
Andre Dicaire