Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5479 subscribers
Views
9267 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Anonymous
13 Jan 2021 8:15 PM
AMS Device Manager V14 Download
0 Replies
Harry
8 Jan 2021 2:06 AM
Status: OPC Server init failed: hr=8008005. Error Msg: Server execution failed
11 Replies
Shawn Connor
7 Jan 2021 6:16 PM
S Series AI Charm failure
6 Replies
BillS
7 Jan 2021 6:01 PM
DeltaV Download
11 Replies
David Tudor Evans
5 Jan 2021 3:48 AM
Upnp Template Language in the Delta V Workstation
2 Replies
<
>
Similar Posts
Creating FrsModules_Theme Dynamos
Module Parameters in Dynamo that generate a skip error, but still work
PCSD Dynamo and the Update Dynamo Expert
Can I edit dynamos in a dynamo set?
Create a module for Diagnostic Parameters
Share
create modules dynamo
hi dears
how can i create a dynamo that can support two modules ?
every module has its data link.
1 Reply
Bill Tinley
30 Oct 2015 11:56 AM
I don't think I have ever done this for a dynamo, but I have done a similar thing for faceplate/detail displays...should work the same way:
It is easy if you can make the name of the second module start with the name of the first module. For example, a pump module (P-100) with an external interlock module (P-100-ILK). Then a single reference for @MOD@ will work for both modules: @MOD@/DC1/SP_D.CV for the pump module, @MOD@-ILK/CND1/OUT.CV for the interlock module, etc.