Emerson Exchange 365
Search
User
Site
Search
User
Replies
1 reply
Subscribers
5479 subscribers
Views
9243 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Brian Hrankowsky
7 Jun 2021 1:55 PM
Does it makes sense that the DC block can trip when already commanded to passive
18 Replies
MPHymel
4 Jun 2021 11:51 AM
Can MODBUS Function Code 8 be disabled on VIM2
2 Replies
hast66
24 May 2021 12:11 PM
a few newbee questions
2 Replies
ctgarvey
18 May 2021 6:56 AM
OPCUA client/server communications to 3rd party systems in DeltaV simulate V14.3.1 how to import 3rd party trusted certificates
6 Replies
Andy M Smith
15 May 2021 6:36 AM
DeltaV Live - DeltaV Scheduler
5 Replies
<
>
Similar Posts
Creating FrsModules_Theme Dynamos
Module Parameters in Dynamo that generate a skip error, but still work
PCSD Dynamo and the Update Dynamo Expert
Can I edit dynamos in a dynamo set?
Create a module for Diagnostic Parameters
Share
create modules dynamo
hi dears
how can i create a dynamo that can support two modules ?
every module has its data link.
1 Reply
Bill Tinley
30 Oct 2015 11:56 AM
I don't think I have ever done this for a dynamo, but I have done a similar thing for faceplate/detail displays...should work the same way:
It is easy if you can make the name of the second module start with the name of the first module. For example, a pump module (P-100) with an external interlock module (P-100-ILK). Then a single reference for @MOD@ will work for both modules: @MOD@/DC1/SP_D.CV for the pump module, @MOD@-ILK/CND1/OUT.CV for the interlock module, etc.