Hi,
Can I use DeltaV SIS logic solver as Analog Output?
In reply to GeloCortez:
As Roshan pointed out, the AO on the DeltaV SIS is a two-state output, low (4mA) and high (20mA) with HART; the AO does not modulate and you therefore cannot use it for regulatory control.