KROHNE OPTIWAVE 7300C FF H1

Hello;

I have a fieldbus communication with different instruments.
but the problem is that for the level transmitter KROHNE OPTIWAVE 7300C I could not find at the library and even on deltav deviceinstallkitsearch .

thank you for your cooperation.

Best regards.

Butler faith.

  • Butler I would just use the device files from fieldbus.org - if you are running DeltaV version 10.3 or later, it's been tested to function with DD's from the fieldbus web site.

  • In reply to John Rezabek:

    John Rezabek thank you very much for your response.
    even on site I found the Optiwave 5200 I could not found 7300.

    Best regards.

    Butler faith.

  • In reply to Butler faith:

    Perhaps it has not yet passed interoperability testing (and received an FF checkmark), or maybe the FF lab hasn't updated the website (there may be some adjustment following the formation of FieldComm Group). I would contact Khrone; they suggest an email  [email protected]. There is a DD file on their website.

    It's a good practice to consider specifying that "fieldbus devices shall carry a checkmark from the FieldComm Group / FF certifying that it has passed interoperability testing". This is especially important if you don't have your own lab where you can do your own testing.