Hello Everyone,
Version DeltaV10.3.2
I am facing problem on Profibus DP card, after each 2 to 3 mins Redundant Card of PRofibus Shows Error on PHV "REDIO :card No Comm ; Cardc3"
when this error comes Red led Blinks for 6 to 10 sec then automatically gets Cleared. before this issue comes card were working ok since installation of Deltav
When I switch Redundancy of Card from Diagnostics ,i get same issue of Redundant cards which is active card previously.
I have checked Cards on Different Ctrl but not Showing any Issue like this.
is it some Communication problem?,6 devices are present on This Profibus card and only one port is used.
pls help me to solved this problem.
Hi, check the terminal block. disconnect the profibus cable and check for errors. Delete the redundancy errors from the card in diagnostics by pressing right mouse.. "delete errors" check the supply and see if there is any additional information in diagnostics.
edit. check that the card/controller has the right software version
Niklas Flykt
Klinkmann Oy
[email protected]
In reply to Niklas Flykt:
In reply to bhushan619:
