Emerson Exchange 365
Search
User
Site
Search
User
State
Verified Answer
Replies
2 replies
Subscribers
5482 subscribers
Views
11134 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Rein
29 Nov 2021 2:27 PM
Moving the Full Span of Control License from one Professional Station to another Professional Station
2 Replies
spaul-WME
19 Nov 2021 4:58 PM
User-Defined Export / Format File issue - DEVICE_STATUS
0 Replies
John Rezabek
11 Nov 2021 2:35 PM
OPC Mirror in DeltaV 14.3.1 / LTS - how to set up users?
4 Replies
Senthilkrishnan M
10 Nov 2021 12:09 PM
How to Use DC block to configure permiisive for both open and close commands
6 Replies
ktidke
9 Nov 2021 5:22 PM
OAR display for confirmer and verifier password button is not responding from Live
2 Replies
<
>
Similar Posts
Two System ID in same PLANT LAN and Same proplus name
Connecting two 1420 WirelessHART Gateways on the same fiber backhaul to the DeltaV Primary / Secondary network
Show and write the same parameter for diferent products in display
Delta V Operate support multiple instances of the same faceplate
Can Delta V Operate support multiple instances of the same faceplate?
Share
Answered
Two faceplate is displayed in the same time
Hello,everyone!
I met a problem. I want to display two same faceplate at the same time.for example.dispaly the two Valve's faceplate or two Pump'sfaceplate,But I don't know how to finish it.
All Responses
Answers Only
AdrianOffield
1 Jul 2014 7:11 AM
Inside the usersettings graphics, inside the script (right mouse button on graphic page and -> Edit Script), you will find reference to multiple faceplates (look for a line “frsVariables.GN_IA_LOCKENABLED.CurrentValue = 1” and uncomment it).
That should give you what you want.