Using AI 16 CH Active Cards for some 4 wires signals
Dear All,
in my project, some signals have been added that generated by analyzers. these signals are 4 wires (it means DCS cards should be Passive), but i have only some AI cards 16 CH with 2 wires Terminal Block ( Active AI Card).
is it possible to use the existing AI modules (Active AI Cards) for these kind of signals? if Yes, how can i use the 16 CH AI cards for 3 wires signals?
Thanks and Regards
Pouya
  • You would need some sort of isolation barrier or converter to relay the 4 wire signal to a 2 wire signal for use on the AI card.
    Sent: Tuesday, May 27, 2014 7:08 AM
    To: [email protected]
    Subject: [EE365 DeltaV Track] Using AI CH Active Cards for some 4 wires signal
    Dear All,
    Thanks and Regards
    Pouya
  • In reply to Pouya:
    HI,
    YES, you can use them you connect the Analog measure + signal to the Even numbers (- ) and connect the measure - wire to the shielding bar.
    You feed the suplly from some other place to the field device..
    Niklas Flykt
    Klinkmann Oy
    [email protected]
  • Given that the AI card also supplies power to the device, won’t this cause other problems if powered externally?
    Sent: Tuesday, May 27, 2014 8:17 AM
    Subject: RE: [EE365 DeltaV Track] Using AI 16 CH Active Cards for some 4 wires signals
    HI,
    YES, you can use them you connect the Analog measure + signal to the ODD numbers (- ) and connect the measure - wire to the shielding bar.
  • In reply to AdrianOffield:
    when I have connected them like there has been no problems.
    If you want it totally passive you have to change the base plate to the passive version..hmm 16..8 channels?
    EDIT: You might have to have the supply from the same power source as the cards...Geeked
    Niklas Flykt
    Klinkmann Oy
    [email protected]
  • In reply to Niklas Flykt:
    Dear Niklas
    Thanks a lot
    Hence for example, for channel 1,  i will connect the Signal (+) to Terminal Number 2 (NOT 1) and then connect the Signal(-) to shield bar, NOT to terminal number 2. am i right?
    Dear Pouya,
    That is right, it should work if you field equipment isn´t using some odd voltage in analog loop. (e.g. Siemens s7-1200 AO is 15 volts max... ).
    Connect one loop and see if it works.
    Niklas Flykt
    Klinkmann Oy
    [email protected]
    Very Good, Many, Many Thanks Niklas.
    i will inform you about my test.
    Best Regards
    In case this question was raised for an M-series 16 Channel AI Card, we have a new Terminal block available which will be able to deal with a 4-wire Transmitter,
    in the same straight  forward way, like for a 2-wre Transmitter !
    Checkout the following PDS and Page 25:
    www2.emersonprocess.com/.../PDS_M-series_Traditional_IO.pdf
    VE4003S2B6 vs. VE4003S2B7