Errors are appearing when we try to open assigned modules of Simulation Pro+
Best Regards,
Rachelle McWright: Business Development Manager, Dynamic Simulation: U.S. Gulf Coast
HI,
The first error seems to pointing to that there are multiple users accessing the same module at the same time.
Are there also a PRO station installed or can you access the modules from the OP stations.
Is the module open in some other window/ computer?
The #2 and #3 error is pointing to the databse files, if the harddrive (virtual drive) is OK then it´s propably that the database is corrupted.
You could try to run the "fix database tool" and see if that helps.
Error #4 and #5 is pointing to same as error 2 and 3.
Is this message appering in every module or just some modules?
If you have the backup FHX-file, import it and try if that one works.
If the problem is only one module, you could try to open the FHX file and take a look on it and compare it to a working block.
What is the system layout...? versions etc.. have you installed all the updates and hotfixes, is the SQL running...?
Niklas Flykt
Klinkmann Oy
Key Account Manager safety products
[email protected]
In reply to Niklas Flykt:
Smells like database corruption. Did you have power failure recently? Or ProPlus was not shutdown properly?