Trouble Getting PID faceplate Update

Dear all,

I am currently having an issue regarding the PID_Loop faceplate update. I have made some little modifications (e.g increasing the number of lines for description) in the faceplate . Now when i go into runtime and click my custom icon i get the correct modified faceplate the first time but for the next three to four clicks i get the generic faceplate again. Is this a HMI scan rate issue? Kindly help me with thing.

Regards

Muhammad Asim Butt

  • Update Popup pictures, you need to run this in order to update the temporary faceplate files.
     
    Alternatively, you can create copies of the original faceplate and put them into the temp (D:\DeltaV\DVData\Graphics-iFix\Pic\Temp\Faceplate) directory as *_fp1.grf, *_fp2.grf and *.fp3.grf
     
    From: M_ASIM_B [mailto:[email protected]]
    Sent: Tuesday, December 24, 2013 10:48 AM
    To: [email protected]
    Subject: [EE365 DeltaV Track] Trouble Getting PID faceplate Update
     

    Dear all,

    I am currently having an issue regarding the PID_Loop faceplate update. I have made some little modifications (e.g increasing the number of lines for description) in the faceplate . Now when i go into runtime and click my custom icon i get the correct modified faceplate the first time but for the next three to four clicks i get the generic faceplate again. Is this a HMI scan rate issue? Kindly help me with thing.