Pro Plus download problems to my OPS with grf files, are not updated allways (DeltaV 9.3.1)

When we start a downlaod from the Pro Plus ( in the back round, runs the yellow page server), we don`t find after more hours the updated *.grf files on our OPS Stations?

3 Replies

  • Have you checked the auto update settings (from PRO+) and made sure your workstations are set for receiving graphics?
     
    From: Patrick K [mailto:[email protected]]
    Sent: Thursday, October 31, 2013 12:17 PM
    To: [email protected]
    Subject: [EE365 DeltaV Track] Pro Plus download problems to my OPS with grf files, are not updated allways (DeltaV 9.3.1)
     

    When we start a downlaod from the Pro Plus ( in the back round, runs the yellow page server), we don`t find after more hours the updated *.grf files on our OPS Stations?

  • The graphics download function is not instantaneous. It tries to schedule things according to network loading. If you open  yellowpagesdiag on a workstation, you can watch the progress of the download.

     

    Youssef El-Bahtimy | Systems Integration Technologist
    PROCONEX | 103 Enterprise Drive | Royersford, PA 19468 USA
    Proconex Office: 610 495 2970 | Cell: 267 275 7513
    [email protected]

    ------
    Original message ------
    From: Patrick K
    Date: 2013/10/31 05:16
    To: [email protected];
    Subject:[EE365 DeltaV Track] Pro Plus download problems to my OPS with grf files, are not updated allways (DeltaV 9.3.1)

    When we start a downlaod from the Pro Plus ( in the back round, runs the yellow page server), we don`t find after more hours the updated *.grf files on our OPS Stations?

     
  • In reply to Youssef.El-Bahtimy:

    I have not checked recently but, in earlier versions of DeltaV, the time stamp on the files made a difference.  On a development system, we accidentally had the time zone of one of the Op Stations set wrong and it was not being updated by yellow pages because YP saw the files on that station as newer than the ones on the ProPlus.