We have observed a difference in SX Controller behavior between DeltaV versions 14.3.1.7332 and 14.3.1.7412 related to EDC / CAS_IN_D functionality.
When the CAS SP Track device option is disabled, EDC1 / CAS_IN_D is not modifiable in DeltaV 14.3.1.7412 during the LO Mode ( Interlock active ). However, in the previous version (14.3.1.7332), CAS_IN_D could be modified under the same conditions.
In our pump logic, the CAS SP Track option is not enabled, and the EM HOLD command is used to drive CAS_IN_D to the passive state during interlock activation. After upgrading to DeltaV 14.3.1.7412, we noticed that when the EDC block enters LO mode, the HOLD logic is unable to write to CAS_IN_D.
Has anyone experienced similar behavior or can share insights on this change?
Thank you,Prasanth