Dear All
I've deltav system with 2 redundant DCS series M controller and other two pairs for ESD , 6 ows, 2 ews, one Pro plus version 14.31 lts
On diagnostic DCS ctrl Keeps giving yellow alarm that redundant fail /not available as shown below.
Then everything goes well for 3 to 5 min then gives the same error again also for 3 to 5 min .
I've removed one ctrl the system runs smoothly by the other .( do not matter you remove active or standby)
Then returned it back , after synchronizing the error is repeated again.
This issue is in DCS ctrl only
note some I/o channels are open and other give error but should not disturb REDUANDANT CTRL PAIR
Also in some place it shows IO error in the standby controller
please advise
Thanks