DeltaV 13.3.1
We had a power blip today and we experienced some odd behavior related to Charms IO. The IO is part of a redundant CIOC setup, with 6 terminal bases in series and 2 more mounted to the right connected via extension cables.
It affected two different DeltaV systems with the only common tie was the power blip.
Scenario one:One CIOC driving solely analog outputs, showed healthy on the CIOC comms as well as redundant health. All 6 Charms terminal bases in the field showed a red/green blinking light on the analog output Charms modules. Guessing the flash frequency was about 2 secs. All the channels showed bad on diag with yellow question mark and associated modules were modbad. We tried downloading CIOC and .... Finally, we cycled power on the 2 wide and when it powered up, everything was fine.
The above isn't so bad since it showed in Diag that something was wrong.
Scenario two: Another event was also on a CIOC, but was analog inputs. There was no local indication that the Charms were unhealthy from the LEDs on the individual charms IO modules. Diagnostics did not show any yellow question marks. The control modules showed modbad and inputs to the loops were showing out of range. The 4-20 on the actual inputs were within range. I cycled power on the CIOC and everything came back ok.... An event happened exactly like the analog input description above but on a totally separate system with same solution of cycling power.
Has anyone else seen this? Thanks!
Andre Dicaire