Emerson Exchange 365
Search
User
Site
Search
User
State
Suggested Answer
Replies
1 reply
Answers
1 answer
Subscribers
5481 subscribers
Views
1593 views
Users
0 members are here
Recent DeltaV Community Connect Discussions
Eric Gratz
24 Oct 2022 6:09 PM
Insight Inspect Large Variability - STDEV_TIME setting
1 Reply
John Andrews
23 Oct 2022 12:42 PM
DV V14: Viewing User Manager account history results in system #U
0 Replies
Sophia Prokh
18 Oct 2022 2:29 PM
Unsubscribe me.
1 Reply
Wes Urbat
17 Oct 2022 7:51 AM
Control Module Class External Reference to Unit Module Alias
8 Replies
kathrynpate
13 Oct 2022 2:42 PM
DeltaV Multifunction Input Card Frequency Filter
0 Replies
<
>
Similar Posts
timeout between processor 2 and i/o processor 2 in SLS1508
Share
Answer Suggested
SLS1508
Dear all;
I'm facing a problem with the serial number of logic solver.
I've faced with the SLS508 with the different s/n in hardware side and software? Is it possible?
All Responses
Answers Only
CCA
20 Nov 2024 9:19 AM
We have come across this. If you have Guardian, you can download KBA NK-1200-0263 DeltaV Diagnostics May Not Display the Correct Serial Numbers for Some Logic Solvers and SISNet Repeater.
Pasting snippets here for your reference: :)
This Knowledge Base Article, NK-1200-0263, documents an issue where DeltaV Diagnostics may not display the correct
serial number for some Logic Solvers and SISNet Repeaters.
The serial numbers of the Logic Solver cards and SISNet repeaters are available in DeltaV Diagnostics. These values
should be unique. However, it was found that the location information of a certain batch of hardware could not be
decoded by the controller. As a result, different or duplicate serial numbers appear in the card’s serial number
diagnostic attribute.
Workaround:
To determine the correct serial number, refer to the label on the Logic Solver and/or SISNet repeater.
Performing an advanced telnet to the affected Logic Solver and/or SISNet repeater will also provide the correct serial
number information. For assistance in performing this procedure, please contact the Global Service Center.
Note The discrepancy in the serial number shown in Diagnostics does not have any impact on operations.
Resolution:
Please refer to KBA AP-0800-0154: DeltaV Safety Instrumented Systems (SIS) Software Updates. Follow the link to
Incident TFS106546 to download the latest hotfix.
This issue has been resolved in DeltaV v12.3