DeltaV OPC UA Server identifiers (NodeId)
Hi All,
Does anyone know if the DeltaV OPC UA Server support numeric identifiers for NodeIds?
DeltaV
1 Reply
Tony Whitehouse
12 Aug 2025 6:37 AM
Yes it does.