Good day everyone.
I am currently doing a proof testing on migrating from Serial to EIOC. I had one test where I needed to configure a Device tag, which is an input register, that needs to read register address 001. When configuring device tags from the EIOC (in DeltaV Explorer), it automatically puts the offsets based on the register type (in this case, it automatically makes it 30001 instead of accessing 001). Is there a way to overcome this? I am aware that for Serial cards, we have an option to upgrade its firmware to Programmable serial to be able to do this. Is there a similar solution that can be applied to EIOC?
Hoping for any response and thanks in advance.
Best regards,Clarence
Andre Dicaire
In reply to Andre Dicaire:
In reply to KeithStThomas:
In reply to Chaitanya Adkar:
In reply to Matt Forbis:
In reply to chrishoffpauir:
Emerson announced that this is resolved in v15FP1 ( Im on FP2)
This is not something that will be rolled back into v14LTS, as far as I know
Looks like v15.FP2 should support the full range now.
In reply to Shannon Jistel:
Just to clarify, if I have a Modbus server that uses 6-digit addressing (400001 - 465535), will a pre-v15.FP2 EIOC be able to read registers 400001 through 409999 from that device? Thanks
In reply to Colin Swaney: