Register configure
Hi All
Is it possible to configure one register to be read and write in same time ,by use VIM2.
1 Reply
David Scott
24 Jan 2022 5:24 AM
Have a look in Books Online for Output Readback - this might be what you are looking for, although it applies to a dataset rather than a single register.