Emerson Exchange 365
Sign-In / Register
Site
Sign-In/Register
Community Hubs
DeltaV Community Connect
Ovation Users Group
Asset Management
Measurement Instrumentation
Valves, Actuators & Regulators
Fluid Control & Pneumatics
Electrical Components & Lighting
Welding, Assembly & Cleaning
Perspectives
Emerson Automation Experts
Conferences
San Antonio 2025
Düsseldorf 2024
Immerse - Anaheim 2023
Grapevine 2022
Community Hubs
More
DeltaV Community Connect
DeltaV Blog
Forums
Blogs
Library/Resources
Members
Tags
More
Cancel
Create New Post
Comment or Question? Become a member of this Emerson Exchange 365 group. Click here to join.
Group Members
Kevin Mansson
Kevin Mahoney
Kevin Hawkins
Kevin Girard
Kevin Etheridge
Kevin Doucet
Kevin Copeland
Kevin Chadwick
Kevin Bremser
Kevin Baker
Kevan Kumar
Ketan
Keshav kendre
kerson.godoy@emerson...
Kerina Leong
kerem coban
kentchrisman
kentberry@safecontrol...
kent kean
Kent Fetter
Kent
kennyrk
KENNYD1952
Kenny Welch
Kennetheno
Kenneth Yashim
Kenneth Wonodi
Kenneth Simpton
Kenneth Shin
Kenneth Shadle
Kenneth Acevedo...
Kenbo
Ken Rancourt
Ken Pettus
ken mead
Ken McClure
Ken Lowery
Ken Lambert
Ken Jamin
Ken Hoover
Ken Bicknell
Ken Archie
Kelvin Oakes
Kelsey Weber
Kellyyper
Kelli Settell
Kellen Butler
KeithStThomas
KeithHarms
Keith_Li
<
>
Activity
Tags
Subscribe by email
More
Cancel
By date
By view count
By comment count
Descending
Ascending
New Advanced Continuous Historian Product Data Sheet
Larry Griffin
The Advanced Continuous Historian stores and retrieves large numbers of process measurements quickly and efficiently. (500KB PDF) Read the full text.
1 Apr 2014
Wireless Throttling Valve Power Consumption
Terry Blevins
Something that all manufactures of wireless throttling valves must be concerned with in their design is battery power consumption. In a control application using a wireless throttling valve much of the power available to the actuator is used to track changes in target valve position. To minimize battery power consumption, the number of changes made … Continue reading » Read the full text.
31 Mar 2014
New Advanced Continuous Historian FAQs Whitepaper
Larry Griffin
This whitepaper answers questions about the Advanced Continuous Historian available in DeltaV v12.3.1 and later releases. (126KB PDF) Read the full text.
31 Mar 2014
Utilizing Wireless Throttling Valves in Control
Terry Blevins
Over the last five years a wide variety of WirelessHART transmitters have been introduced by the major manufacturers of field devices. The PIDPlus enables closed loop control using the slower update rate provided by a wireless transmitter. The broad acceptance of wireless transmitters has generated an interest in the application of wireless throttling valves in … Continue reading » Read the full text.
24 Mar 2014
Magnetrol Model 706 Rev 1 Fieldbus Device Files
Larry Griffin
In Emerson’s continuing commitment to open and interoperable standards, the Magnetrol Model 706 Rev 1 has passed the rigorous and comprehensive testing of the DeltaV Stress Test labs. Using the Device Installation Kits for Emerson Products website at http://www2.emersonprocess.com/en-US/documentation/deviceinstallkits/Pages/deviceinstallkitsearch.aspx, these fieldbus device files are now available for use. Read the full…
18 Mar 2014
Flow Control – Positive Displacement Pump Part 2
Terry Blevins
When using a positive displacement pump in flow control, then the minimum flow which may be achieved using a variable speed drive is limited by the motor low speed limit. It is possible to achieve a wider range of flow control by regulating flow using a fixed speed motor and a throttling valve in combination … Continue reading » Read the full text.
17 Mar 2014
Flow Control – Positive Displacement Pump Part 1
Terry Blevins
Positive displacement pumps may be used when it is necessary address flow requirements of 2GPM or less. The pump design ( e.g. vane, gear, peristaltic) selected for a particular application should be based on properties of the liquid and the expected operating condition. One characteristic of a positive displacement pump is that when it is … Continue reading » Read the full text.
10 Mar 2014
Flow Control – Centrifugal Pump
Terry Blevins
Centrifugal pumps can be used to transfer large volumes of liquid between vessels in an industrial process. When a constant speed motor is used to drive the pump then the pump flow rate may be controlled by adjusting a throttling valve that is installed after the pump discharge, as illustrated below. The pump discharge pressure … Continue reading » Read the full text.
3 Mar 2014
Wireless Control – ACC 2014
Terry Blevins
The 2014 American Control Conference, ACC, will be held Wednesday through Friday, June 4 – 6, at the Hilton Portland & Executive Tower, Portland, OR. As noted on the conference web site, the ACC is internationally recognized as a premier scientific and engineering conference dedicated to the advancement of control theory and practice. Last year … Continue reading » Read the full text.
24 Feb 2014
High Speed Wireless Control
Terry Blevins
I was recently sent a link to a YouTube video of a control demonstration by professor Raffaello D’Andrea, The Institute for Dynamic Systems and Control at ETH, Swiss Federal Institute of Technology, Zurich. ETH is one of the world’s leading universities for technology and the natural sciences. I found the demonstration by Professor D’Andrea to … Continue reading » Read the full text.
17 Feb 2014
DeltaV system historian options expanded
Chris Felts
Over the years, the DeltaV system has evolved, and so has the platform used for collecting and storing real-time process data generated by DeltaV controllers, workstations, and non-DeltaV data sources. The DeltaV system currently provides three historian options: the DeltaV Continuous Historian, the Advanced Continuous Historian, and the enterprise historian. Each historian represents different levels of functionality…
10 Feb 2014
The Changing Web
Terry Blevins
It is quite easy to upload and store a power point presentation as a Slideshare file on the Slideshare web site. Once a presentation is uploaded in this manner then it may be viewed by anyone through the Slideshare web site. In addition, the Slideshare web site includes tools that that allow an audio recording … Continue reading » Read the full text.
10 Feb 2014
WirelessHART – Monitoring and Control of On-Off Valves
Terry Blevins
A number of WirelessHART devices have been introduced over the last few years to monitor the status of on/off valves. For example, the TopWorx 4310 WirelessHART Valve Position Monitor can be used detect linear and rotary movement using non-contact technology with limit switch feedback. Such devices provide a low cost way to monitor the position … Continue reading » Read the full text.
3 Feb 2014
WirelessHART – Level Switch
Terry Blevins
In many tank level control applications, a level switch is installed and used as an interlock to help prevent overfilling the tank. For example, in many existing installations you may find a vibrating fork liquid level switch wired as an input to the control system. However, today it is possible to reduce the cost of installing a … Continue reading » Read the full text.
27 Jan 2014
Krohne UFC400 Rev 1 Fieldbus Device Files
Larry Griffin
In Emerson’s continuing commitment to open and interoperable standards, the KROHNE UFC400 Rev 1 has passed the rigorous and comprehensive testing of the DeltaV Stress Test labs. Using the Device Installation Kits for Emerson Products website at http://www2.emersonprocess.com/en-US/documentation/deviceinstallkits/Pages/deviceinstallkitsearch.aspx, these fieldbus device files are now available for use. Read the full text…
22 Jan 2014
WirelessHART – Discrete Measurement
Terry Blevins
Many manufacturers initially introduced WirelessHART field devices that were designed to support continuous process measurements such pressure, flow, temperature, and level. Also, WirelessHART transmitters are now available for analytical measurements such as pH. Recently you may have noticed that some manufacturers have introduced WirelessHART field devices for discrete measurement. For example, Rosemount has released…
20 Jan 2014
2014 Emerson Global Users Exchange Americas – Call for Presentations
Larry Griffin
The 2014 Emerson Global Users Exchange Americas needs your excellent presentations and user content to continue the tradition of our high quality, user-driven conference. The theme of this year’s Emerson Exchange is ‘Inspiring Ingenuity‘ – an opportunity to meet with industry professionals and peers in an exhilarating environment where creativity, inventiveness and talent work in [...] Read the full text.
17 Jan 2014
Wireless Measurements in Control Applications
Jim Cahill
As wireless technology continues to be used in process manufacturing facilities, those used in control applications are increasing. At the ISA Automation Week conference, Emerson’s Terry Blevins, Mark Nixon, and Marty Zielinski authored the paper, Using Wireless Measurements in Control Applications. Terry and Marty presented it for Automation Week attendees. They discussed the impact of […] Read the full text.
8 Jan 2014
Finding a Patent
Terry Blevins
When exploring a new area of technology, it is often helpful to find out what patents have been granted or are pending. The patent office allows anyone to explore the patent office database free of charge. A quick search capability is provide that allows you to easily find out what patent have been granted to … Continue reading » Read the full text.
6 Jan 2014
New DeltaV SIS with Electronic Marshalling for Migrations Product Data Sheet
Larry Griffin
With DeltaV SIS with Electronic Marshalling for Migrations hardware, you can migrate to DeltaV SIS without having to add cabinets, custom cables, or extra marshalling. (900KB PDF) Read the full text.
6 Jan 2014
New M-series Mass Connection Solutions Product Data Sheet
Larry Griffin
The DeltaV M-series Mass Connection Solutions make connecting field devices to I/O cards fast and easy. (910KB PDF) Read the full text.
6 Jan 2014
Emerson Exchange 2013 – Workshop Videos
Terry Blevins
Emerson Exchange was held this year at the Gaylord Texan Hotel and Convention Center, Grapevine, TX on Sept 30th – Oct 4th, 2013. Over 350 workshops were hosted over a three day period. In addition, on the last day of Emerson Exchange, a small number of Meet the Expert workshops were presented. This year the … Continue reading » Read the full text.
30 Dec 2013
Willy Wojsznis – ISA Fellow
Terry Blevins
The International Society of Automation (ISA) Fellow grade is provided to qualified senior ISA members who have made exceptional engineering or scientific contributions to the field of automation that advance the state of the art. Nomination requires a minimum of five Fellow evaluators or a combination of nine Fellows and Senior Members. The candidates nominated … Continue reading » Read the full text.
16 Dec 2013
More on Foundation Fieldbus and HART
Jim Cahill
I wanted to bring visibility to several recent comments from an earlier post, Major Difference between Foundation Fieldbus and HART Protocols. Here’s the summation thought from the first comment: …With one software package, and as put above with HART pass-through, you can document EVERY HART instrument on site, and THEN with Plantweb, monitor the lot […] Read the full text.
11 Dec 2013
Using Wireless Measurements In Control Applications
Terry Blevins
Wireless transmitters may be preferred in applications where new measurements are required since the cost may be lower than that associated with installing wired transmitters. However, there is a significant differences in the frequency and manner in which a new measurement value is updated by a wired transmitter vs. a wireless transmitter. Such differences must … Continue reading » Read the full text.
9 Dec 2013
<
>